I'll try all of that today. Thanks for getting back to us.

((Sorry meant the X66 port as the KLI port! We aren't plugging anything into EtherCAT at the moment.))
#2
Hi Johannes,

We thought we had the eCat error fixed once we successfully jumped the X55 connector. The message away and were able to run automatic programs for a few days. It was working great.

The problem returned when I started configuring the controllers for Roboteam. I did two things on both controllers. Not sure what caused the error, but now they both have it again:

1.)   I renamed both controllers from the pendant Start-Up wizard to KUKA1 and KUKA2. Previously, they were named after the controller serial number. We are eventually going to have students working and I wanted to make the machine ID more clear.
2.)   I connected the controllers to an ethernet switch via CAT5 on the X65 (KLI) connection.

As prompted, I saved the changes to the RDC and then performed a controller restart with the file refresh / update option checked. After reboot, the SYS-X44 error came up. Once again, we can't run programs in AUT.

**********

I tried the following to attempt to fix the issue. None of these worked:

1.)   Checked the X55 connections; both seated correctly. Same error with them plugged in or not. (hardware likely not the cause as it affected both systems after the software change)
2.)   I unplugged the X65 connections and renamed the controllers back to their original names and reset, etc. (tried to return it to the earlier state)
3.)   I changed the X44 restart value in KRC\Roboter\Config\User\Common\ECAT_SYS_X44.xml from "manual" to "auto", restarted etc.
4.)   I opened the current project in WorkVisual, removed the X44 interface and re-added it. eCat came attached to it by default. I deployed the project and restarted the controller.

I'm not certain whether I need to fix something else in WorkVisual, like you said. Perhaps we aren't properly running the shutdown sequence to recompile / deploy the files?

Do you have any ideas for things we could try?

Thanks!
Nick